True but however don’t you think 25-50V is very high. As far as I know it shouldn’t cross 3 volts.
I have done almost every tests. Please do check out the below thread. I have checked the direct neutral line from EB post with earth disconnecting everything in the apartment
Dear Fm’s As the title suggests my earthing is all messed up. Neutral to earth reading as per IEEE standard should not exceed 3 volts for homes and 5 for industrial. Mine is always around 15-30. I contacted vertex and had their electrician inspect my grounding. As per his suggestions we...
www.hifivision.com
True, N-E voltages should be in the range you quoted.
I read through the other thread you mentioned quickly. I guess the issue is with the EB.
There could be some high resistance fault among two phases causing the neutral to rise. Check the phase to phase and phase to neutral voltages at your main incomer. This can give a clue.
Else the neutral earthing of EB transformer is the culprit for the reasons I wrote earlier. Not sure if you can get this to the regulator's notice.
Another culprit for your hum could be the wiring in the house. The usual malpractice of the electrical contractors - to loop the neutral whereas wiring regs all over the world says every circuit should have own neutral running to the DB. But over there they save wire and loop the neutrals. You pay for a point but they save the black wire and make a profit. When there is some motor say fridge or mixie running that obviously produce some harmonics and the interference can seep into the sensitive audio equipment. Try running a separate circuit with own neutral to the DB of your house with an extension chord. Later maybe try to reach the DB through the conduits with a separate neutral wire (possibly impossible).
I also read in the other thread about twisting wires causing issues. It is a perfectly acceptable method of jointing in the industry for wires up to like 2.5sq.mm
if done properly. Having worked in India I can imagine what's happening there. One thing not used is the heat shrink insulation. Electricians use the normal insulation tape and stretch it over the wires. This gets undone over a period of time and water seeps in.
And copper or steel in earthing pit does not matter. Copper corrodes less, hence longer life. Earthing is basically to conduct away the fault current and magnitudes can be in the range of kA. So the material becomes immaterial if it is sized properly to meet the thermal requirements.
Earth resistance is the interface resistance between the metal surface and the general earth. Chemical earthing as they say is used in very dry areas and rocky places - basically is bentonite clay mixed with some additives to enhance conductivity as it absorbs and retains moisture from water seeping in to the ground as well as fills the voids (air is an insulator). They drill the rock, fill with the so called chemical and insert the earth rod. For Chennai with the clayey soil it may not add value.